40G Ceritfier Copper Test Failures
My copper tests keep failing on my Viavi Certifier 40G. What can I do to troubleshoot?
My copper tests keep failing on my Viavi Certifier 40G. What can I do to troubleshoot?
viavianswers Feb 21, 2017 10:11 AM
Correct Answer
First make sure the correct limit is selected for the type of copper cabling that you are testing. Second make sure a proper reference was performed and if necessary re-reference the units. Check all connections at panel and jack fields. Wire should only be untwisted just enough to perform the termination and no more. Use the fault locator graph, on the cable test results, to identify the distance to the worst result which is most likely a connection of some type and re-terminate. If permanent link testing, check the probe count under the SYSTEM SETTINGS>SETTINGS 2<>DEVICE INFO. Viavi recommends that permanent link adapter cords be replaced after 5000 tests.